R
ryanryan
On installation of a 125amp 3P Dist. board I have recorded a PFC of 12kA and PSCC of 8kA (approx 16kA at 400v).
The DB is 20m away from the transformer ( hence the high values) and is supplied via a 100/125A MCCB, with a short-ircuit rating of 36Ka.
My problem is that the mcb's for the DB are rated at 10kA.
Do Square D mcbs go above 10kA?
The DB is 20m away from the transformer ( hence the high values) and is supplied via a 100/125A MCCB, with a short-ircuit rating of 36Ka.
My problem is that the mcb's for the DB are rated at 10kA.
Do Square D mcbs go above 10kA?