P
pablo4321
Hi been to a job today checked the ring down and i got a really high reading
on the r1 end to end continuity
r1=955 ohms
rn=0.45
ee=0.59
what could be possible causes for this reading could it just be a loose connection
at a fitting or something else,what would be best way to tackle this thanks for any replys.
Poor connection would be my first thought, hopefully at an outlet rather than an inaccessible junction box under the floor somewhere.
**** although looking again that figure is very high ****
Have you done any further tests?
shortcircuit thanks for your reply, no i havent as yet going back tommorow to have a proper look just done these tests as am wanting to add a couple of sockets to this ring so had to get some cables in as the plasterer was waiting to get done what would you recommend
Use a trailing lead,split the lives at a mid point and take a reading to determine which half is the problem
Take readings of the bad half and note which have the high readings,the problem will likely be at the highest reading of those good sockets or at the lowest reading of the bad sockets
I've had a reading like that before on a neary plastered wall on the CPC, i was making a circuit through the dampness of the plaster with a socket on the other side of the room lol
I would say a lose connection or a stray cable just resting against the terminal.
As said above try a wondering lead - the other option if you dont have a wondering lead is do a R1+R2 on only half the ring and go around the sockets connecting the L&E together (at each socket) till you get the high reading then check that socket then the socket before. (you can always jumper at the CU and test each socket individuality using a plug - might be easier and quicker.