Hi I'm getting a big tns ze reading of 46.35,they have previous certificates of the last electricians work (consumer unit upgrade) which shows they got a reading of 111.2 ohms and signed it off.
What do you recommend I do here?
Has anyone else come across this?

Thanks
 
if it's TN-S then get DNO to fix it. are you sure it's not TT. though?
 
The earth facility is for the DNO to maintain at lower than 0.8 ohms. Call them and ask to speak to the duty engineer.
Are you sure this isn't a DIY TN-S?
 
Sorry didnt see the replies. I sorted it now. It was definitely a tns, It's impossible to mistake a TT for a tns in my opinion you shouldn't be a sparky if you do. They've been out and put a temporary link in and are going to have to investigate further the problem. Thanks for the replies anyway.
 
Sorry didnt see the replies. I sorted it now. It was definitely a tns, It's impossible to mistake a TT for a tns in my opinion you shouldn't be a sparky if you do

To be quite honest mate, in my opinion you shouldn't be a sparky if you don't know what to do when you get a Ze of 46 ohms on a TN-S system!
 
Hi I'm getting a big tns ze reading of 46.35,they have previous certificates of the last electricians work (consumer unit upgrade) which shows they got a reading of 111.2 ohms and signed it off.
What do you recommend I do here?
Has anyone else come across this?

Thanks

Signs of a distinct improvement then!! lol!!
 