Hello was just wondering as been told to do a couple of different things wen the ze is high on a install just wondering what everyone's thort where??? Thanks
 
do you think that's enough info for us to answer? earthing system? Ze readings? what's the question?
 
Ok then it was tn-s and was 1.73 disconnected all earths and bonding so just main earth was just the external ze all covered by rcd so ok but edf need to sort the problem
 
A Ze above 0.35 on a T-N-CS or over 0.8 on a T-N-S it is the DNO responsibility to maintain and rectify it, although they must be informed ASAP. On a TT it is the customers responsibility to get it to and maintain it at a reasonable value, 200 ohms is the figure in BS7671 although a value alot lower is suggested by many on here.
 
all down to how you are working. if on your own, then contact DNO. if you work for a firm, report it to your immediate superiors. if you have done a cert. get them to countersign it.
 
just make sure you've got the right value before contacting them. is your tester calibrated?
 