Hi everyone, can anyone tell me how much actually needs bonding under 17th edition?
I know water and gas need bonding with 10 mm and bathrooms need all metal pipes ect bonding but what about boilers hot cold water pipes from boilers ? and rads in other rooms?
I have asked several different people and got different answers.
Help much appreciated
Paul
 
main bonding required to gas water oil services etc, usually 10mm, although this is not always necc you can calculate the actual required size using the adiabatic equation.
supplemntary bonding is now no longer a requirement unless disconection times can not be met which is unlikely with rcd in circuit.
 
We bond gas and water 10mm, but under 17th you don,t have to cross bond bathrooms, and as above said supplementary bonding is not req, but as there seems to a lot of people using plastic water pipes, a bit of copper and a bit of plastic here there and every where, we still cross bond all the pipes, copper ones in the Imm/Htr cupboard usually, bit of belt and braces job really.
 
Thanks ,
so no rads need bonding?
I thought it was a case of dependent on continuity from pipes and rads ect to MET and that kind of made sence. ie if very high resistence dont bond (less chance of shock) but under a certain amount bond?
If it was say 1 ohm and there was prob with cpc rcd would still trip but if 1000 ohm rcd may not trip and you get full fault current through your body for as long as you touch ?
Paul
 

Reply to How much bonding? in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Hi folks, I'd like to get my Nest thermostat up and running with the gas combi boiler (Worcester Greenstar HIghflow 440 Standalone). FYI - I...
Replies
9
Views
1K
Hey everyone, hope you all had a good xmas. Got called around to change over an old style pin type thermostat to a hive one for a family member...
Replies
1
Views
528
Apologies if this is in the wrong section - appreciate it's more of an educational question. That said I have 2391 - but the classroom environment...
Replies
2
Views
2K
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock