At least they put an insulating partition between services! and I am sure the top of that board is IP4X!
Lovely job.
Isnt it ip2x for top surfaces

At least they put an insulating partition between services! and I am sure the top of that board is IP4X!
Lovely job.

just this little bit of nonsense going on in a cellar....
looks like a Electrical Trainee board change....
View attachment 19027View attachment 19028View attachment 19029
I would say that one could actually be IP2X as it is not really very accessible but for horizontal accessible surfaces the protection required is IP4X, 416.2.2.Isnt it ip2x for top surfaces![]()
Doing an eicr in a hotel and the maintanence guy asked if i could take a look at an intermittantly tripping rcd.
Rcd tested fine, so i started disconnecting the fittings for an ir test and found this.
![]()
200mm of kingspan, and unenclosed connector blocks sitting in the kingspan directly above a 50w downlight.
Anyone else had any fun findings this week?
Tim

it was IP f**kall X....you could get a finger in there....I would say that one could actually be IP2X as it is not really very accessible but for horizontal accessible surfaces the protection required is IP4X, 416.2.2.
I would say that one could actually be IP2X as it is not really very accessible but for horizontal accessible surfaces the protection required is IP4X, 416.2.2.

waste not want notI hope you're going to use that again
And whatThis idiot connected up a 3 phase motor for a spray booth using such great joints!!View attachment 19023
i`v got a board change on tomorrow.....i`ll get some before n after pics....show you how it should be done...