Does anyone know which IEC standard has the original body graph that table 41.1 in BS7671 is based off of? When was the body graph last revised? Can anyone link or post the body graph here?

Also anyone know how the body graph was originally created?
 
Table 41.1 refers to maximum disconnection times for fault conditions. If by body graph you mean some graph of resistance in the human body, I believe it's irrelevant to the table, because the disconnection elements (MCBs, fuses) are not there to protect humans, they are there to protect the installation and connected equipment.

MCBs and fuses cannot protect a human who comes into contact with live parts unless they pass currents large enough to trip the device, by which time they will likely be dead, severely injured or very lucky.

I'm happy to be proven wrong, but I'd also be interested in the point you're looking to prove/question.
 
Table 41.1 refers to maximum disconnection times for fault conditions. If by body graph you mean some graph of resistance in the human body, I believe it's irrelevant to the table, because the disconnection elements (MCBs, fuses) are not there to protect humans, they are there to protect the installation and connected equipment.

MCBs and fuses cannot protect a human who comes into contact with live parts unless they pass currents large enough to trip the device, by which time they will likely be dead, severely injured or very lucky.

I'm happy to be proven wrong, but I'd also be interested in the point you're looking to prove/question.

Disconnection times are linked to touch voltage during a fault, the whole system of ADS and bonding works together to limit the voltage rise on all exposed parts during a fault in any part of an installation.
 
Table 41.1 refers to maximum disconnection times for fault conditions. If by body graph you mean some graph of resistance in the human body, I believe it's irrelevant to the table, because the disconnection elements (MCBs, fuses) are not there to protect humans, they are there to protect the installation and connected equipment.

MCBs and fuses cannot protect a human who comes into contact with live parts unless they pass currents large enough to trip the device, by which time they will likely be dead, severely injured or very lucky.

I'm happy to be proven wrong, but I'd also be interested in the point you're looking to prove/question.

If I am correct, I think this is the table that 41.1 is based upon... however I don't know out of which IEC document it originally came from or if its been updated since.

View: https://Upload the image directly to the thread.com/EsfizW5
 
Disconnection times are linked to touch voltage during a fault, the whole system of ADS and bonding works together to limit the voltage rise on all exposed parts during a fault in any part of an installation.

Yup. Touch voltage in relation to physoligcal effects on the body driving disconnection time.
 
There is a graph of electric shock risk here:

The boundary of the green region crosses at 30mA / 0.4s and by 5s the exposure time is making no real difference. The red danger region for 0.4s is around 120mA, and the same Wikipedia article has the conductivity limit (high 5% case) for humans as around 1.2k ohm at 100V (i.e. hitting that 120mA limit).

These may not be a coincidence...
 
There is a graph of electric shock risk here:

The boundary of the green region crosses at 30mA / 0.4s and by 5s the exposure time is making no real difference. The red danger region for 0.4s is around 120mA, and the same Wikipedia article has the conductivity limit (high 5% case) for humans as around 1.2k ohm at 100V (i.e. hitting that 120mA limit).

These may not be a coincidence...

IEC60479-1 is the original standard? Any idea what testing they did?
 