hi everyone I have a question: Water heater 3kw the length of the circuit is 28m , the line and cpc 2.5mm2 How determine the expected Zs? I'm looking for in On-Side Guide but I do not know..... any suggestions please Thanks
 
I'm wondering why you need the OSG to work out the calculated Zs value of a circuit?? This is, or damn well should be basic knowledge to you!!!
 
You've got to get the data from somewhere haven't you? The guy is in training, you can't expect him to have learned the resistance of conductors off by heart!
 
Robs given you the Zs = Ze plus r1 r2 , if you do your r1 r2 ,switch supply off disconnect the main earth and take your Ze from the main earth block if the cut out if it has one or main earth cable removed from earth at board and across live and neutral , once ze has been done then reconnect your earth add the Ze to the r1r2 and that will be the calculated Zs you can the do the live Zs the result could be different due to parallel earth paths etc
 

Reply to Impedance Zs in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top