If you have a high resistance on a neutral in a 3 phase system, even if no items are 3 phase the common neutral bar becomes a central point for all things connected, so a current will go up from one phase off through a load back down the neutral then up the next item on a diffrent phase (the lowest resistance path) If an item on the second phase is a high load (low resistance)(or inductive)this will produce a high voltage across the other items even up to 400v if the neutral is shot.
 
Last edited by a moderator:
Sounds like a hung Neutral could have done it, this is one reason why I would never put a neutral through a contactor with 3 phases as 230 volt could easily become 400 if the coil packs up and the poles don't connect properly, out of interest is there a contactor at all in line with the DB?
 
Last edited by a moderator:
a phone call to the contractor who tested it 6 8 months ago would be interesting ive no doubt they will say the same well it was allright when we tested it interesting

It probably was. When does it cease to be the inspectors responsibility? He cant be held accountable for the duration until his next recommended retest date. If its anything like the car MOT, its only valid at the time the test was carried out, and i see no reason why electrical installations should be any different. No end of stuff could have been done in the eight months since it was I&T'd. I know what my reply would be if someone tried to hold me to account in this situation. It would get me a long ban on here from Jason anyway.

Cheers..........Howard
 
problem is if you loose a neutral on the DNO side especially on TNCS three phase you can get a back feed down the other phases so basically you end up with 400 volts across the appliances on a single phase , other things that can happen is flashing florescents if the are switch start normally go bang if HF and the voltages can peak way higher than 400 had a domestic board with RCBOs all RCBO's tripped when the neutral; was lost measured 680 volts across the switch and it set fire to the incomming supply of a garage 2 doors away
 
Seen a lot of equipment in a comms room / IT room, Go BOOM due to no neutral, smoke and everything.
 
If you have a high resistance on a neutral in a 3 phase system, even if no items are 3 phase the common neutral bar becomes a central point for all things connected, so a current will go up from one phase off through a load back down the neutral then up the next item on a diffrent phase (the lowest resistance path) If an item on the second phase is a high load (low resistance)(or inductive)this will produce a high voltage across the other items even up to 400v if the neutral is shot.

I was trying to word that the otherday, but eventually gave up! nice one :D
 