It's not ideal but appendix. C on GN3 says:
Where safe access is available to enclose the live conductors in a current clamp, but not the protective conductor, a suitably rated earth leakage current clamp meter (sometimes called a tong tester) can be used to provide an indication of the state of insulation in a circuit downstream of the test point, by measuring ‘earth leakage’. An example is shown in Figure C1.
In small installations, readings of a few milliamps will indicate protective conductor
currents, but readings of many amps may indicate a line-to-earth or neutral-to-earth fault.