In process of doing an EICR in Hotel Environment, how are we suppose to carry out IR Tests, Main Panel DB’s & other DB’s cannot be isolated during this Report.
 
It's not ideal but appendix. C on GN3 says:
Where safe access is available to enclose the live conductors in a current clamp, but not the protective conductor, a suitably rated earth leakage current clamp meter (sometimes called a tong tester) can be used to provide an indication of the state of insulation in a circuit downstream of the test point, by measuring ‘earth leakage’. An example is shown in Figure C1.
In small installations, readings of a few milliamps will indicate protective conductor
currents, but readings of many amps may indicate a line-to-earth or neutral-to-earth fault.
 
Mmm Limitations on one of the most important tests on condition reports. IMO and its just my opinion if you cant IR test not much point on doing an EICR.
Yea it’s one I’m not happy with TBF… doing this report there are other major issues which will need addressing.
Also LIM to me is better than all other EICR Certs I’ve seen > 200 .. absolutely no way
 