ENG, I think he's saying that the upstairs ring IS run in the loft (and down the studwork). Daz
 
ENG, I think he's saying that the upstairs ring IS run in the loft (and down the studwork). Daz


Where a loft conversion is made, insulation material can be removed where cables are run for the loft conversion. Once inside the stud work walls of the conversion your well and truly out of the insulation problem. I very much doubt if the upstairs RFC is run all the way up to the loft area and then drop down to the outlets. More likely that the existing ring is either extended, or fuse spurred off the existing ring to cover the one or two rooms of a loft conversion.

May even be done properly and run separate circuit's for the lighting and sockets (ring or radial) for the loft conversion.
 
Yes, but Eddiesparks was referring to his own post (see post #3). Daz

Your right, should of checked back over the past posts!! ...lol!! Is it usual now, to fill stud walls in domestics with insulation?? I know they never used too, unless specified by the architect...
 
Where a loft conversion is made, insulation material can be removed where cables are run for the loft conversion. Once inside the stud work walls of the conversion your well and truly out of the insulation problem. I very much doubt if the upstairs RFC is run all the way up to the loft area and then drop down to the outlets. More likely that the existing ring is either extended, or fuse spurred off the existing ring to cover the one or two rooms of a loft conversion.

May even be done properly and run separate circuit's for the lighting and sockets (ring or radial) for the loft conversion.

Its actually quite common in 'cottages' where access between the floor/ceiling is more or less non-existent. I remember one property where we had no access under the floor so we ran the cables up to the loft and dropped them down the walls. You'd be amazed where cables are run in old pre-victorian houses.
 
Your right, should of checked back over the past posts!! ...lol!! Is it usual now, to fill stud walls in domestics with insulation?? I know they never used too, unless specified by the architect...

eng., it's becoming increasingly common to find the crap stuffed in stud walls. why anyone would want to prevent the escape of a little bit of heat from 1 room to another when both rooms should be at similar temperatures evades me entirely.
 
my answer to that would be that a cable rated at, say 12A if using a 10A breaker, is rated at 12A continuously, and is capable of carrying the 15A for the short period ( < 1 hour ) that it would take for the 10A breaker to trip at 15A.

Thats what i thought but, using our example, if there was a load of 14a the 12a cable would be overloaded by about 15-20% but breaker would not even trip at all. As i said, a 10a breaker's minimum trip (straight line on bgb graphs) is about 15a ( and it's def not less than an hour - more like 10000 seconds) -

Real life example- 32a breaker and 4mm cable clipped direct. 40a continuous overload. Anyone?!?!

Something tells me the IET wouldnt leave any margin for error!!!
 
The CCC in BS7671 are intended to allow a circuit to run as expected without risk. The regulations require that circuits are designed not to have a small overload of long duration.
There is still a lot of leeway on the CCC of the cable, however one should not take this into account because that is what the regs have done to simplify things ane prevent inadvertent fires.
 
Ok that's as i thought but wanted it clarified. Cheers Richard. I wonder what the REAL current carrying capacities are then. Probably a fair bit higher higher! Anyone can be arsed to do the maths knowing resistivity of copper etc? Haha
 
OK so P in watts = joules per second
P = V￾²/R
specific heat capacity of copper is 0.385J/gK
density of copper is 8.963g/cm³
Find out the level of heat loss from insulation and sheath and discover when the temperature of the copper reaches 70 c and you are there!
 