UK Intermittent RCCB Trip

Hi

Over the last 2 or 3 years, my earth leakage breaker has been tripping maybe 5 or 6 times a year. This could be at any time of day, including the middle of the night and also a few times when on holiday when there’s no-one around which is the last time it happened and doesn’t do the fridges and freezers any good. Whilst generally inconvenient, and aside from the obvious, it is the trip during holidays which makes me feel the need to identify the problem.

My consumer unit was installed 20+ year’s ago. The MCBs are F&G, and the earth trip (Xpole PFIM-80/2/003) is only on the power circuits (5No – Garage (20A Xpole), Cooker, Kitchen, Up and Down) which I believe is no longer recommended but, at least, it narrows my search.

I have a pond wired through a 30mA Power Breaker as a spur from the kitchen circuit running pump, air-pump and lights (lights have been turned off for over a year now) and my feeling is that if damp was causing the trip then it would not be possible to reset until it dried out and I would hope my breaker on the spur would trip too.

When it does trip, almost without exception, it is possible to reset it straight away without it tripping again and so nigh on impossible to identify the fault. Could it be a faulty RCCB randomly tripping?

I’ve tried testing with an AC Leakage Current Meter but unable to locate any anomalies.

I’m wondering if it is practical to directly swap the MCBs with RCBOs in the hope that the problem circuit can at least be identified although I’m guessing that would probably need the RCCB to be bypassed/removed unless more sensitive RCBOs are available.

TIA
20260512_113339.jpg
 
Intermittent faults are the hardest to find. If it is happening often, try this, as it's the main switch tripping, try switching off items with elements ie the cooker, water heaters, etc. If it stops tripping, switch back on one at a time.

If it's random, an investigation of your installation will be needed
 
Intermittent faults are the hardest to find. If it is happening often, try this, as it's the main switch tripping, try switching off items with elements ie the cooker, water heaters, etc. If it stops tripping, switch back on one at a time.

If it's random, an investigation of your installation will be needed
Really not practical for trips approx every 2 to 3 months and I feel an investigation would be a waste of everyone's time at this stage, but thanks anyway.
I'm getting to the point of unplugging everything not in use or needed for my holidays. However, the problem is that so many things are required to be left on so it's practically only the garage and cooker circuits which can be turned off.
 
I would completely disconnect the spur feeding the pump. The power breaker may only have live switching, so any dampness affecting the neutral will still be picked up by the main RCCB.

Any other external sockets supplied from any of the socket circuits?

An electrician will have an RCD tester that not only will time the trip, to make sure it trips within the 40ms regulatory limit, but also how sensitive it is. A 30mA rated device could be as low as 20mA with measurement. Anything lower than 15mA would fail the RCCB device.
 
I would completely disconnect the spur feeding the pump. The power breaker may only have live switching, so any dampness affecting the neutral will still be picked up by the main RCCB.

Any other external sockets supplied from any of the socket circuits?

An electrician will have an RCD tester that not only will time the trip, to make sure it trips within the 40ms regulatory limit, but also how sensitive it is. A 30mA rated device could be as low as 20mA with measurement. Anything lower than 15mA would fail the RCCB device.
Disconnecting the pond spur is not practical for a long period and certainly not for months, as it provides 'life support' to the fish in the forms of filtration and aeration. I understand the neutral leak principle but, as mentioned, if damp was the issue, why only for the moment?

Yes, there's an IP56 socket on the same spur fixed to the house.

Getting the RCD tested is a good idea.

I'm still interested in the possibility/practicality of RCBOs to help isolate the problematic circuit. I'll discuss with whoever tests the RCD
 
It is likely that if you suggest adapting the board to accept rcbo’s, the recommendation would be to change the entire board.
That would make it a metal board, with SPD fitted and all circuits on an individual RCBO.

The problem is, you will still have an underlying problem with the affected circuit that still needs investigated.
 
It is likely that if you suggest adapting the board to accept rcbo’s, the recommendation would be to change the entire board.
That would make it a metal board, with SPD fitted and all circuits on an individual RCBO.

The problem is, you will still have an underlying problem with the affected circuit that still needs investigated.
So a metal board is within the latest regs? Sounds like a bigger job than I hoped for.

Yes, but then only one circuit can be concentrated on with the possibility of turning it off when I go away.
 
Did the testing with the 'AC Leakage Current Meter' show any leakage at all, eg in the order of milliamps on any of the circuits?
With the installation in its normal functioning state, with everything plugged in and operating, I would expect to see a background residual current (ie 'leakage') from suppressors in appliances and electronic devices. If your measuring device didn't report any current, I would question its sensitivity.

Motor operated appliances (washing machine, dishwasher, food processor) are permitted up to 3.5mA 'leakage' each. Electronic devices and chargers can typically 'leak' up to 1mA. Supressors may be fitted in the appliance prior to the power switch, so the current flows even when the appliance/device is switched off. Simlarly if you turn the outlet it's plugged into 'off', only the live is usually switched, meaning there is still a capacitor between neutral and earth, and the sum total of all those in the house can exacerbate a separate fault induced tripping problem. Hence advice to unplug appliances and accessories when testing the wiring.
The installation can build up a total 'leakage' of 5-10mA, meaning an additional leakage fault somewhere doesn't need to be enormous to trip the main residual current device.

I would encourage you to investigate the outdoor wiring and pond pump/filter acessories. As long term pond owners, we've got through several Blagdon pumps and UV filters that suffered leakage current, and only last month had to replace a year-old UV light ballast, which caused random tripping every few weeks (which incidentally could be instantly reset).
 
It could be an accumulation of earth leakage exceeding the trip value of the RCCB (could be as low as 18mA) (See post #8)
For example circuits 1+4+6 would cause it to trip, but then again in another scenario circuits 2+4+7 could cause it to trip. There may not be an exact pattern!
The EL for each circuit needs to be measured to see if an accumulation of EL current is the cause and not one particular circuit at fault.
 