The EFLI needs to be low enough for the protective device to operate in the required DT. The PFC should not be higher than the Icn of the protective device. This is so that the device will safely interrupt and clear the fault without potentially blowing to bits.
 
Q. State the two conditions that need to be taken into account when comparing measured and maximum permitted Zs values?
 
http://www.electriciansforums.co.uk...-useful-information-2394-a-20.html#post640526

The answers to most, if not all your questions are somewhere in that thread. If you open that thread and look near the top of the page you'll see it says 'search thread'
Drawing1.jpg

If you click on it it will give you a small text box where you can type or paste what you're looking for;
Drawing2.jpg

If for some reason you don't get the results you were hoping for, also in the same place you can go to an advanced search window which will only search that thread still;
Drawing3.jpg

From that window you can run a more refined search.
 
thanks for the advice, I have tried it but not getting what Im looking for
 