I have broken into a ring, to feed an RCD spur to then go on to feed other items, but cant say as I would do it quite this way.

I am sure you have logical explanation in your head somewhere...
 
There is a bit in app15 (RFC part) that suggests appliance greater than or equal to 2kW should be fitted on their own dedicated radial circuit.
 
Basically he wants to run a rfc in kitchen for his appliances but use fcu's supplying double sockets. Instead of pulling appliances out to get to sockets he wants to fit fcu above worktop then run cable in wall to double sockets. If that makes more sense

There must be literally thousands of kitchens wired up exactly that way to provide isolation to under-counter appliances without having to touch the appliance. The other method is to fit appliance sockets in adjacent kitchen cabinet & drill out of sight hole to allow plug to pass through.
Either method is acceptable
 

OFFICIAL SPONSORS

Back
Top