DieselShunter

If I want to install one double socket on its own new circuit for a Washing Machine and a Tumble Dryer, (max load approx 5.5kVA) what are the views of me running this off its own 32Amp MCB and cabling it with a pair of paralleled-up 2.5mm cables doubled up (to provide sufficient current capacity and Vdrop) over a 20mtr run from the CU. Curious to know others views on this. :wink5:
 
stick it on a 2.5mm radial. 20A MCB. sorted. RFC for a couple of machines that will only pull 18A in the unlikely event that both are heating simultaneously is overkill.
 
sorry, didn't see the wattage. looks a lot for w/m and t/d. still comes down to 23A at worst. bet if you clamp them it'll be even less.
 
You may be able to use 4mm cable but check max load over the distance and install of cable. or just use 2 seperate 2.5 cables off of 1 32 amp breaker. It's allowed in the regs.
 