3 phase DB supplied by 35mm tails run in the same trunking as all the conductors for the installation fed from an isolator about 40 metres away at the supply origin , my mentor who thinks he knows everything says this is against the regs , running it in the same trunking , i cant find anything to back this up does anyone know if this is fact
 
no problem if all cables have been sized acccording the grouping and the trunking is of the correct capacity.
 
I'd say that's absolutely fine as long as they are all mains cables within the trunking and no ELV.
 