D
Darkwood
As mentioned in other post page 42 green OSG states 'where there is plastic incoming service and a metal installation within the premises main bonding is recommended unless it has been confirmed that any metallic pipework within the building is not introducing earth potential.Really DW?
I would say that if your start bonding metal work that wasn't an extraneous conductive part then you more likely to make that piece of metal live during a fault. We after all don't bond metal door frames, windows etc, as they have no contact with earth, and so bonding a metal pipe within an installation, that as no connection with earth, ie main pipe coming in plastic, but internal installation is copper, is IMO not needed.
Of course it is always best to check if the pipe is an extraneous conductive part, but if it isn't it don't need bonding
This is one of those regs that can be misread in my mind, as a golden rule always bond Gas/Water regardless of incoming pipe unless internal pipework is also plastic, consider a live wire under the floor touches a water pipe which has no bonding and has incoming plastic supply... there will then be a floating PD of 230v from say your tap and a adjacent cooker's metal work, its no rocket science to work out the consequences of this situation as ive been called out to exactly this issue, with regards to doors and windows in metal... their was alot of confusion many years ago regarding said bonding and at one point it was necessary but this was soon shelved as the likelyhood of windows and doors becoming live and a risk to safety was neglegible as well as been screws/bolted to the building mass too which would give a easier earth path than joe bloggs opening door.
Yes agree circumstances do exist where you dont need to bond gas/water if incoming plastic and metal internal but it would require thorough checking that it dosnt introduce earth potential and is prone to other trades altering their installs and making bonding a requirement.... so to sum up i reckon its best to do it regardless of incoming pipe.
Last edited by a moderator: