A
ANDY FIRST
No power given for that motor m8!?!...
Hi i=p/u, Ensure you don't use the terms "phase rotation test or tester" C&G are hot on this, PHASE SEQUENCE TEST or TESTER are the approved terms. Also approved testers are the rotating disc type and indicator lamp type (See 612.12 and GN3 2.7.17).phase rotation instruments, 1)audio phase rotation instrument 2) visual phase rotation instrument...
The Chief examiners report states that the instrument names accepted are those listed in chapter 4 of GN3 and therefore would be a phase rotation instrument.Phase rotation instrument is the correct term as per GN3 section 4.8, if you have a look at the following. In the first paragraph on the last couple of lines it states that the phase rotation instrument can be "Mechanical, visual and/or audible". phase sequence is the type of test not the measuring device.
do knowanyone know where i can find the labelled diagram of earthing , cpcs , bonding conductors that was in the red bs 7671. its obv not in green bs 7671