Lighting contactors

is there any downside of running a 10amp lighting circuit then down stream of that a smaller breaker in an enclosure to feed the contactor then a switch controlling the contactor? Loads 5x400 watt lights.
 
Last edited by a moderator:
is there any downside of running a 10amp lighting circuit then down stream of that a smaller breaker in an enclosure to feed the contactor then a switch controlling the contactor? Loads 5x400 watt lights.
Why not use a 20amp switch.
 
Using a contactor means the simple switch could be replaced by a smart switch, sensor, or timer in the future which may not be able to switch the full load.
 
You made no mention of a sensor in your original post. You can do it like this but if the sensor can switch the load it isn't necessary. If you decide to go this route the additional mcb isn't necessary.
 
Perfectly fine and sensible if the photo cell is rated less than 10A but if not, just a waste of a circuit breaker, although provides local isolation for the control circuit.
 
The extra circuit breaker is not necessary for the photo cell
In my opinion, overload protection is not required when it is only driving a contactor coil.
 