LogiDrive 2000 FFF error

  • Thread starter Thread starter scarebyte
  • Start date Start date
  • Tags Tags
    error
S

scarebyte

Hi i have a LogiDrive 2000 (Lenord Bauer) drive and it only shows in its panel: FFF, I think is a kind of overflow.

Any ideas?

Regards.
 
http://www.lenord.de/en/produkte/motionline/antrieb/LD2000/db2000_e.pdf

This will help!
 
Without fault codes you will have to get your tester out and start tracing the fault. I would attack in this order.

1. Check everything is plugged in. This is a complex drive with many feedback options. If any of the sockets are not in use verify why?
2. Check all supplies are present. This is the 3 phase, 24 volt and any comms (CAN bus or RS 232/485).
3. Check contractor is energised.
4. Check control signals. E-stop, stop, enable and run will be a minimum. Additionally there is options for analogue, digital and comms control.
Good luck and let us know how you get on.
 