Hello , got something to clarify ....My boss and I have always fitted Isolators for fans , and used low voltage fans in bathrooms and other places where needed , he got into a discussion in a wholesalers yesterday with another electrician who thought it would be ok to put a fan in a shower (no isolator) as the circuit was protected by an RCD , .....the discussion turned into an argument .
Wondered what your thoughts were if any ,
Cheers
 
All manufacturers vary but if the instruction are read through, they will tell you want zones the fans can be used in.

As for isolation, then yes every time for me also.
 
I don't see how providing additional protection by means of a 30mA RCD would have any effect on a requirement to provide local isolation?
Either BS7671 requires local isolation or it doesn't.
 
I don't see how providing additional protection by means of a 30mA RCD would have any effect on a requirement to provide local isolation?
Either BS7671 requires local isolation or it doesn't.

Thats how it turned into an argument !, Im asking because i like to think ive been taught correctly , we just fit LV as my boss says its good practice ,.
The other guy was a Lithuanian electrician and obviously thought he was doing it ok as he wasnt open to any input !
 
I guess it all depends on what purpose the isolation is intended to serve.
If it's just to allow maintenance, then no it's not really required, but the fact that the circuit is RCD protected would neither here or there.
If it's to allow functional awitching, then again the fact that the circuit is RCD protected is neither here or there.
If however it's to allow emergency switching, then yes perhaps having the circuit RCD protected would entail that local isolation is not required.
As for whether the fan should be LV or ELV, I guess that's really just down to personal choice. Either are acceptable as far as BS7671 is concerned.
 
i would always put an isolator in but in zone 1 i thought you could install mains voltage fan as long as its at least ip44 can someone tell me any different ?
 
It's fine, as long as manufacturers instructions are observed. Same applies to local isolation - putting BS7671 aside, the instructions nearly always require local two pole isolation and 3amp fusing. That topic was done to death in a recent thread.
 