I have been asked to re wire a house which has its existing consumer unit (no rcd, re wireable fuses) supplied by an M.I.C from the garage where the meter is fitted. This is approx 4m from consumer unit, unable to identify size of the conducter yet, but in order for this to comply with regs will an mcb suitable for the size of conductor to protect the M.I.C between meter and c.u be sufficient or do i need to change the cable completely?
 
an upfront switch fuse rated at 60A or 63A would comply with the 3m rule. if the MIC is incapable of carrying 63+A, then you'll need to replace it anyway.
 