It does have a lot to do with the unstable parameters mentioned, such as poor earthing, lack of bonding etc.
Essentially the shock voltage difference between an TN & a TT system is roughly double, i.e a TN system with a good, reliable, low impedance fault path, with both line & CPC of the same CSA (disregard T+E here), would have a shock voltage of roughly 115V
TT would be almost as makes no difference be 230V which would travel through the installation & via the high impedance earth electrode, which is why we must reduce the disconnection time for clearance of an L-E fault.
I believe the 5s rule for TN systems was to allow the continued use of a 3036 re-weireable type fuse. It's reduced to 1s for TT to allow for discrimination to be achieved.