Hi I am just doing a renovation / upgrade on a small house and as kitchen plus all downstairs was on same ring final I have broken it up into a separate kitchen ring and downstairs ring and renewed best part of the cabling as it was really old stranded earth steel looking junk cable and not giving good test readings. I need to replace the main CU from a 3036 board and a separate garage sub board and also add storage heaters although not as many as client wanted as it was hitting over 90.5A just on store heaters !

I have hassles from DNO as they won't tell me upfront what size the service fuse is without submitting all loads I need to feed, and I need to ask if I have radials for say the garage skts do I apply diversity such as 1st ring final @ 100% and then 40% of all other ring finals and also 40% of radial wired socket outlets ?

There will be a ring in the utility room as there will be 2.5mm feeding sockets for a washing machine and a dryer but I know that the two are rated at 2.2kW ( washing is rated at 2.2-2.6kW ) can I use those figures direct as flc ? and such as upstairs ring may be calculated at 40% but most likely pull less than 5A most of the time.

Thanks...
 
Its sealed amlu so bit naughty cutting a DNO seal ! I've seen bosses do it a few times before but I'm going to source a 4 pole switch to isolate the tails as and when for future so best not cut their seal before they come out to reconnect the seals on fuse and meter tails cover.
 
Take diversity with a bit of flexibility, in a small domestic house the load will not be high, just take account of what the storage heaters will be pulling and other likely loads at the time they are on.
The rest of the demand shoudl not be a worry.
If the head is labelled at 60A then use that, if 60/80A then use 60A, if 100A then probably 100A.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Soulsurfer

Arms
~
Joined
Location
Channel Islands
Business Name
M.B.S ELECTRICAL

Thread Information

Title
Max demand etc.. on renovation.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Soulsurfer,
Last reply from
Soulsurfer,
Replies
4
Views
852

Advert