Gents,

Can anybody advise me on the max CCC of 16mm2 T&E, 8 meters in length clipped direct. Its a sub-main to a consumer unit. Ran off the sub board is a 32amp ring, 2 x 6 amp lights, 2 x 20amp socket radials, 10 amp boiler supply and a 40amp shed supply and smoke detection(6amp).

Cheers
 
85A is about the max. clipped direct. table 4D5, BRB
 