not sure if there is one (not in my tiny brain anyway) but by ensuring all bonding is within 0.05ohms then there will not be a difference of more than 50v between parts the equipotential zone would not be all at exactly the same potential but is limited by the safe touch voltage.
 
Just think that people see the 0.05 value and think its written in stone but there is no mention of it in Reg 544 and GN3 is as clear as mud. If it applies to touch voltage where does the 0.05 fit into the calculation I=Uo/Z then R=50/Ia?
 
agree as i cant see how it would fit into the supp bond formula but the figure 0.05, limiting length and 50v figure can be found from various (reputable) sources so in my opinion there must be a connection somewhere
 