pushrod
sorry didn't notice the boiler - what type is it ? I assume it is not a gas boiler as the current demand to that is tiny. If it is an immersion heater it is probs 3 KW with an approx 13A demand. It would probably be worth looking at it and seeing if you can find a power rating on it. Allowing 32A for it would mean that it was a 7kW+ heater (very unlikely unless it was a shower) You are right that there is no diversity allowed on a water heater.