Darkwood
Just had this covo in a different thread no domestic mcb will give discrimination against any other under short circuit and to note the type b,c or d is inrush allowance and nothing to do with the large current that will flow in a short, i could give you the table list of partial discrimination between different size mcbs but most incoming supplies exceed this in fault current so not worth it, just have to realise its not achievable between standard mcb's.You could always investigate a C type MCB for discrimination.