Discuss MCB type ratings (b,c,d) in the Industrial Electricians' Talk area at ElectriciansForums.net
DanBrown
Hi Guys,
I have just been on a call out to a ventillation fan within a kitchen sometime tripping out on startup.
Basically the fan runs at about 9 amp full on-load current, but the start-up it in the region of 100 amp. Could anyone tell me what rating the fan should be on, and what is if any the theory behind selecting the correct rating type of the mcb. It was on a type ''C'' 20amp that i thaught was adequate for that type of startup.
What is the theory behind selecting the correct rating....
Hi Guys,
ok "In" is the MCB nominal rating (say it has a In of 10A)
Type B's have an instanteneous trip current of 3 to 5 times In (so 30-50A)
Type C's are 10 to 20 times (so 100-200 amps)
Type D's are 20-50 times (so 200-500amps)
think those are the values, dont have the OSG in front of me
I thought it was
Type 'B' 3 to 5 times
Type 'C' 5 to 10 times
Type 'D' 10 to 20 times
Have just checked in OSG Page 51 and it is as I have posted.
I thought it was
I am not even going to check Ian, and the book is in front of me:p
I was 'off the cuff' when i wrote the figures down
thanks for the correction:)
hi
i would suspect the fan ,or at least where its air is coming from ,or going to ,i check everything else first ie ,loose connections,then"megger the motor", check the fan on the motor as well ,its probably clogged with grease,
good luck
Check the trunking that the fan is in as if it has not been cleaned for ages it counld be that blades are jamming on the congealed grease which will be in the trunking with it being in the kitchen.
Reply to MCB type ratings (b,c,d) in the Industrial Electricians' Talk area at ElectriciansForums.net
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Hi all New to this forum, looks like a hive of information. I'm wanting to upgrade my garage electrics - I'm not a qualified electrician, hence...
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...