On another issue how do test the loop impedance at a fixed appliance or a light, to fulfill the measured loop impedance column requirement on the schedule of tests. will the calc R1 + R2 suffice?
 
It doesn't require just the R1 and R2 reading it requires the full ''earth loop path'' Ie Zs?? ((R1 + R2) + Ze)
 
Last edited by a moderator:
On another issue how do test the loop impedance at a fixed appliance or a light, to fulfill the measured loop impedance column requirement on the schedule of tests. will the calc R1 + R2 suffice?

Hey.

First of all the calc for Zs (earth fault loop impedance) is Zs = Ze + (R1+R2). R1+R2 is a measurement on its own - line and earth resistance of a circuit.

To measure Zs on a lighting circuit find the end of the circuit, could be in a switch or a light fitting open up switch/remove light fitting and carry out the test.

I'm a bit confused with the fixed appliance bit, as you only need to test the circuit supplying the appliance so test at socket or iosolator for the appliance.

Hope this helps.
 
Measure Ze at the supply terminals and add R1+R2, the result is inserted into the Zs column. There is no doubt that a live Zs reading at the switch or light is best but we are allowed this method - see Guidance Note 3.
 
Measure Ze at the supply terminals and add R1+R2, the result is inserted into the Zs column. There is no doubt that a live Zs reading at the switch or light is best but we are allowed this method - see Guidance Note 3.

They probably figured it out in the four years since this question was asked.......
 
take down the ceiling rose and test. with the rcd's now you will need a no trip tester
oh do you?
i think not...
2 ways to do this with a high current loop tester:

1)calculate the Zs from the Ze+r1 r2

2)wire out the RCD...

i use both methods to get a Zs as neither of my MFTs do a low current loop....
 

Reply to Measured Loop impedance in the Australia area at ElectriciansForums.net

Similar Threads

Hi all , The measured value of loop impedance for a circuit is 2.4Ω. If the temperature at the time of the test was 20°C and the cable is 70°C...
Replies
4
Views
683
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843
Hi just wondering how most are testing fault loop impedance and which testing units are best
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock