Guys I need to find the Max KA of this type of fuse, its 3036. Normally I would put 2 ka but ive been to a property where the PFC is over 3!

Im happy to except it as 2 but the client wants proof.
Any Ideas?

$(KGrHqJHJEMFChPioNCsBQr-vzomGw~~60_12.JPG
 
surely that pfc is before the 3036 fuses.
 
Quote.. Reg 612.11 Requires that the PFC under both short circuit and earth fault conditions be mesured, calculated or determined by another method at the origin and at other relevant points in the installation.
 
yes, but is the Zs of the individual circuits >2KA? close to the origin, it might be, but generally, it will reduce according to the length and csa of the circuits.
 
it may and does, but if they are rated at only 1KA then any Zs of under 0.23 or 0.11 if 2KA will mean it does not comply. and with such a low Ze then any short radial circuit like a cooker or socket close by will mean im way above the max KA. and just hope theres no cable damage as the circuits leave the CU..

Anyway does anyone know the rating?
 
It looks like the carriers you show take BS1361 fuses (which would mean 16.5kA) but you say they are BS3036, according to the OSG they should have a designation 1/2/4 on them for the kA.
If they are in a consumer unit you can apply the 16kA derogation, other than that replace them if you cannot be sure.
 
Makes you wonder just how the 99% + of domestic installations has survived for up to 80+ years (before being upgraded to MCB's) on nothing but BS 3036 fuses?? lol!! We should all be dead, or at least, very lucky to be alive!! lol!!

And there are STILL to this day, existing installations on BS 3036 CU's with DNO DP BS 3036 service cut-outs!!
 
Makes you wonder just how the 99% + of domestic installations has survived for up to 80+ years (before being upgraded to MCB's) on nothing but BS 3036 fuses?? lol!! We should all be dead, or at least, very lucky to be alive!! lol!!

And there are STILL to this day, existing installations on BS 3036 CU's with DNO DP BS 3036 service cut-outs!!


I did phone MEM tec on friday, speeking to the chap his words were they were most def not rated above 2 KA but that was his word and he wasnt sure. Hence the question
Trouble is with more and more installations now being converted to PME from old TNS systems, The earthing is so much more improved. So the PFC goes way up above what the manafacturer intended. 80+ years ago we were fusing Neutrals, bet you still think that is safe. As it was ok then!!!Lol
 
Last edited by a moderator:
Can you not just apply annex ZA and say it has a suitable service head fuse that protects the CU assembly up to 16kA.
Then you do not need to worry about it.
Of course if it is not in a consumer unit this does not apply.
 