Does any know of any RCBOs which will fit alongside these breakers?
Kitchen upgrade and I’ve told them kitchen sockets need rewired alongside putting on rcd protection.
Also recommended the whole board to be changed which they only want anything doing that’s involving kitchen.
 

Attachments

  • 43548BA6-97BC-4C16-8B2C-EC1F4FB091F9.jpeg
    43548BA6-97BC-4C16-8B2C-EC1F4FB091F9.jpeg
    79.6 KB · Views: 94
  • 453CF01B-D83E-4C7E-9B70-797802E3DF2B.jpeg
    453CF01B-D83E-4C7E-9B70-797802E3DF2B.jpeg
    49 KB · Views: 68
SCHNEIDER took over from merlin. their breakers will fit.
 
You’d better check that you don’t need a 10Ka device as the easy 9 are 6 Ka rcbos, not even sure that they fit or should be fitted to the multi9 range, I’d ask Schneider.
 