Have a client that has just bought a property. In the Garden is a corrugated metal shed come garage. There is a 1.5mm three core swa that runs from the property to the shed. Thinking to fit a RCBO on way in consumer unit to protect cable and accessories. They don’t want garage unit fitted ( waste of time with 1.5mm feed) just want light and socket, so swa into metal clad socket, fused spur to feed light. What about earthing the metal shed should it be cross bonded? Would I be creating a circulating earth path as steel wire will be connected to earth in the house? Will carry out ZS on socket and light so if this complies and the RCBO trips at the correct values do I have to carry out any earthing of the shed.
 
theres nothing wrong with using an RCD fused spur shed end....
this would mean they are not having to go back to the house board to reset....
whats the length of run goin to be here?
 
if its 18 meters then it just comes in...just....
at 20 meters its over...

- - - Updated - - -

then theres Zs
 
What current did you use for calculation? I was going to try and transpose the volt drop formula to see what current would be within speck
 
What current did you use for calculation? I was going to try and transpose the volt drop formula to see what current would be within speck
use 3% as your cutoff point and 13A as your Ib (if using an RCDfcu shed end)...so if its 20 meters this comes in at 7.54V
18 meters is 6.78V....
so be sure to measure that cable accurately...
 
Supply to shed 1.5mm was existing and has been inplace for years feeding three twin sockets and a strip light. So client cant understand why I cant just connect it up again. What was your thoughts on earthing the shed?
 
Supply to shed 1.5mm was existing and has been inplace for years feeding three twin sockets and a strip light. So client cant understand why I cant just connect it up again. What was your thoughts on earthing the shed?
well according to my calcs your Zs for the shed upto the RCDfcu should be 1.28 ohms using .8 as the Ze...
 
Supply to shed 1.5mm was existing and has been inplace for years feeding three twin sockets and a strip light. So client cant understand why I cant just connect it up again. What was your thoughts on earthing the shed?
Whats YOUR thoughts on earthing the shed?
 