I have an ND CUBE 400 meter to exchange next week. Its a like for like change. I can isolate the supply to the meter easily with the removable cartridge fuses, however the circuit the meter is metering cannot be isolated. I am not sure what risk is posed with the CT's. They are terminated into a terminal block so i can just pull that block out and insert into the new meter, i just thought i would check i as am unsure if this is the standard with CT's
 
Depends on the CT type as some (iron core) can produce very high voltages at open circuit, there should be a shorting block installed to allow for shorting the CTs secondary before removing the connections. Best check the CT type first before pulling it.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
-
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Meter exchange - CT
Prefix
N/A
Forum
Talk Electrician Forum
Start date
Last reply date
Replies
1

Thread Tags

Tags Tags
meter

Advert

Thread statistics

Created
gazdkw82,
Last reply from
plugsandsparks,
Replies
1
Views
788

Advert

Back
Top