We i did a CDU up grade a couple of weeks ago all tails were in 16mm no seal on the fuse , but the meters were sealed , so pulled the fuse changed the board tails were nice and long so i left them at 16mm and marked on my cert then its up to the DNO if they want to up grade them , having said that after the meter its the consumers responcability so its catch 22 cant change the tails because the meters sealed could cut them then your responcable if any thing goes wrong and as its an offence to cut seals would your insurance pay out so realy until every supply has been upgraded to 25 mm and a switch fitted then what can we do , as for the meter guy connecting up the supply i posted what happended to me in another post , short story DN issued on a EICR i did after the remidial works done LE reverse , no it was a neutral fault in the meter ,installation left with no supply as he installed a switch and the tails were to short nice one eh