martspark

Done job swa feed up garden to ip skt and lite from ring in diningroom. all buried and glandid properly.
Can i put this on a minor works cert. I no its notifyable and will do through elecsa but to me its only a extention of existing cct and not a new cct so dosnt need eic.

Can i do just a minor then? thanks
oh yeh its protected with fcu in dining room. done all testing aok. zs alright and rcd protected cct. just weather will minor works cert be ok
 
Last edited by a moderator:
If all you've done is extend an existing circuit, then a minor works is fine. But if you've gone to a sub board, then installed a socket circuit and a lighting circuit, you'll have to do a full sheet and a continuation sheet. How exactly have you fed the socket and light?
 
I read it as :
FCU in dining room from existing ringmain, supplying 1x socket & 1x light in garden.

This warrants a minor works cert & as you say notifying under part P.

I do however have a question what is the fuse rating in the fcu at the dining room?

If it's 13amp you'll need to change it to 5 or 3amp unless you have installed another fcu between the new socket & light or the light is on a plug lead plugged into the socket.
 
yeh thats te job! and ive put in 2 fcus for both-1 x13a to protcet everything then to 1x3a just for lites
Have put it all on a minor workd cert i figured that wud be ok and you all agreed Thanks
 
Minor works certificate if you are breaking the circuit. Full cert if you are doing otherwise
 