P
pinball25
hi all im just doing my portfile for my nvq and im a little unsure on something
if i was to change an mcb for a cooker ciruit like for like what cert needs to be issues with it
thanks chris
personally minor works
just remember this simple rule:
1 circuit = minor works
1+ circuits = EIC
Saying that you can do a EIC if you want but your making more work for yourself
i was going to do a minor works but dont want the assaser to knock it back
for wrong cert
if the assessor knocks you back for doing a minor tell them take a run and jump.
also if they do ask them why when 7671 says that is the correct cert!
1+ circuits = EIC
1 new circuit is still EIC. Same as adding to 3 existing circuits would be 3 minor works, or use the MW cert that accommodates 3 circuits
1+ circuits = EIC
Completely incorrect im afraid.
Any new circuit requires an EIC.
And changing the CPD also requires EIC.
Any other alterations / additions to an existing circuit then MWC.
Hence 1+ (good point)
Just making work for yourself
Post this cert up - as I have not seen this one before - I have the EIC and Minor Works
Pm me you email mate and I will send you a copy when I get in the office on Monday, I forget where I got ours from however I have seen elecsa ones before so assume elecsa also do the same 3 on 1 cert.
Napit also have, and the NIC are working on a 1 page EIC for a single circuit
Changing the OCPD can be on a MWC or so I believed and so our NIC man said. All tests required to prove the effectiveness of the new OCPD are carried out and recorded on a MWC so IMO a EIC is unnecessary
Depends on the device RISE , if changing from mcb to rcbo then MWC ok
Anything else ie rewirable 3036 to bs88 fuse or type c mcb then EIC
But i admit thisis a bit of a grey area so all opinions are valid.
Do what YOU thinks best , hardly life or death is it lol.
I cant see the point behind a EIC for say changing from 3036 to 60898 or from a B to a C... What does an EIC ask for that a MWC doesn't that it relivent to this change?
pinball25,
Guest55,