30HP would be about 22kw giving FLC 38-45amp, if this is the case and its is DOL or Star/Delta starting then I'm not surprised its tripping a 63amp mcb, such a motor started with such methods could warrant its own HRC fused supply and not tapped of a dist' board, knowing all the motor and control characteristics is key to knowing if an mcb is suitable.
Need more info, like has been mentioned, check what controls the motor and what size O/L protects it and this should give you an idea.
Also need to know the history, has the motor always done this job, is the product the same as before or has it changed recently to a stiffer mix, does the motor start under load or is it presented to the mix after starting, when exactly does the mcb trip...start up or after running a while?