The resistance per metre of 10mm G+Y single core cable is 1.83 m'ohm per metre.
20M x 1.83 / 1000 = 0.036 ohms. Your value of 0.78 is way off. Check meter accuracy, lead connections, probe tips etc.
Did you disconnect one end of the conductor before you tested it???
I'd agree with this comment. Most 'strange' continuity readings from a low reading Ohmmeters are due to
1/ Not zeroed
2/ Poor croc-clip connection
3/ poor connection of probes to point of contact
4/ high resistance leads
5/ out of calibration meters
Several ways of checking this is
1/ are the high values consistent?
2/ pressing the grip of the croc-clips or repositioning the probes
3/ taking more than one reading
other considerations can be
1/ the differential temperature of the instrument with the ambient temperature, is the instrument cold when first being used?
2/ are the batteries flat?
Simple check would be to get a 100m roll of known sized cable, I use 4mm2 grn/yell.
Knowing the Ohms per meter, the length and a correction factor for the ambient temperature you can then compare the calculated value with the measured value. If there is a significant difference then either you or your instrument is at fault.