Hi,
Can anyone tell me what this thing is: Multi9 CT 20A AC1
I have two of them installed in a CU I'm working on that are fed by 32A mcbs and in turn they feed two storage heaters. I have tested for 230V going into them from the 32A mcbs and there is power there, but there's nothing coming out of them. I've never seen these things before so help would be appreciated in determining what they are if they are faulty.

image1mte.jpg
 
They are standard contactors they only let the power through when the coil is energised..... Im a little surprised you are confused here ...there's even a wiring diagram on the front showing you what it does, are you really telling me you never learnt about basics of a simple contactor at college? Your 'A1' and 'A2' are you coil connections check the coil voltage rating and then check for the voltage at the coil terminals if its not there then it won't let the power through. The AC1 is a rating associated with the ability of the internal contacts to withstand differing types of voltage i.e. Resistive and Inductive.
 
Last edited by a moderator:
and you need a short course in basic photography. get it in focus and keep the camera still.
 
Something is ringing alarm bells here ... you have a 32amp mcb feeding each of the contactors which are only rated for a 20amp load? something about this set-up seems wrong what is the nature of the circuit; cable size, storage heater size, how many heater on each contactor if more than one?
 
Something is ringing alarm bells here ... you have a 32amp mcb feeding each of the contactors which are only rated for a 20amp load? something about this set-up seems wrong what is the nature of the circuit; cable size, storage heater size, how many heater on each contactor if more than one?
This is an existing install that appears to be some years old - it's wired in red and black for a start, my initial thoughts were that the set up seemed wrong and unnecessary as each contactor supplies a radial circuit and there is only one heater on each circuit (there is a 13A spur at the heater). Cable is standard T&E 2.5/1.5
The only reason I haven't bypassed these contactors and wired them directly to the 32A mcbs is that there is a third cable terminated in the first multi9 contactor that I haven't been able to identify. The whole set up seems wrong to me and I'm not sure what the installing electrician was trying to do. Neither of the heaters have worked for some time, a few years at least, but the previous tenant didn't bother reporting it.
 
and you need a short course in basic photography. get it in focus and keep the camera still.

Gee thanks. I'll try better next time, and take something other than a pair of steps and a camera phone just in case I need to be David frickin Bailey, I'm sure my canon sureshot will fit on the van.
 
well at least the over-rated mcb won't be an issue if only 1 heater on each contactor, ideal if you could de-rate to 16amp mcbs... I assume the coils are energised via a timer(clock) this my be set to off?
 
well at least the over-rated mcb won't be an issue if only 1 heater on each contactor, ideal if you could de-rate to 16amp mcbs... I assume the coils are energised via a timer(clock) this my be set to off?

No, they run straight to the fused spur on each circuit. I thought there must be a timer on the circuit somewhere but it's a one-storey flat and no controllers are present.
As for de-rating to 16A mcbs, that's my preferred option too as it seems to be pointless paying £60 each for two new contactors that aren't really necessary.
 
Is the fuseboard where the Contactors are fitted off peak or what ever the new term is. If not then some times storage heaters had a boost switch which would allow the heater to be powered in the day to boost the heating on a cold day when the bricks had cooled. This could be why the spurs feed the coils
 
No, they run straight to the fused spur on each circuit. I thought there must be a timer on the circuit somewhere but it's a one-storey flat and no controllers are present.
As for de-rating to 16A mcbs, that's my preferred option too as it seems to be pointless paying £60 each for two new contactors that aren't really necessary.

You will need somekind of timing circuit so the storage heaters are not on 24/7, power the coils direct just to test the contactors are working which I suspect they will, then work out how you will set a timer up to energise the heaters at night only.

Where do the wires on A1 terminals come from as this is your control and how it used to pull the relay in to let power through to heaters.
 
There must have been a timer or some other form of control, to enable the heaters to have worked in the first place!! If there is room in the DB, you can fit a din rail mouted timer(s) to control these contactors...
 
There must have been a timer or some other form of control, to enable the heaters to have worked in the first place!! If there is room in the DB, you can fit a din rail mouted timer(s) to control these contactors...

Maybe that's why they haven't worked for a few years. I can only tell you what I have found. The heaters appear to be wired so that they are either on or off, and controlled by the fused switched spur beside each heater as to which state it is in - on or off, only now they don't work at all. There is a timer below the CU but that's controlling a heated tower rail in the bathroom(which doesn't heat up but that's another issue) and I can hear the timer working ok but it's on a completely separate circuit.
I wouldn't have wired this flat the way it has been wired but I wasn't the original electrician who wired it.
 
Again ill ask about the wires onto the coil of the contactor ...A2 would be neutral but A1 is the wire that pulls the contactors in .... trace this to see what controls the contactors
 
as darkwood says. you need to trace the coil cables and find out how and if they are energised.
 