Hi everyone,

I'm left feeling a little concerned after an electrician visited us to rectify a problem with our ring main, An RCD was tripping solely when the Ring main was on, there were two other breakers for the lighting circuits which would stay on just fine. I figured it would most likely be an appliance causing the issue so turned off every wall socket, then unplugged everything in the house. The RCD would still trip. This was as far as i could investigate so called a local electrician, they came out every quickly.
They were only at the house for about 30 minutes changing things around in our main board, he mentioned that we could probably use more sockets as our house is quite dated and has only one socket in most rooms, so lots of extension cables are being used.
He removed the socket circuit (ring main i think) from that RCD and left it just on a breaker.

my rail previously looked like this <RCD><Light><Light><unmarked (this was the wall socket breaker> gap <RCD><Unknown Breaker><Main Switch>
After the visit it looks like this <RCD><Light> gap <RCD><unknown breaker (now controlling wall sockets)><Main switch>

The left most RCD turns off the lights, the right most RCD doesnt seem to turn anything off when tested. The right most breaker is now what turns my wall sockets off.
I did not test the right hand cluster of RCD and breaker before the electrician came, so i cant be sure what they were connected to or how it was changed.
My main concern now is that my ring main is not covered by an RCD, and that the RCD was tripping with everything unplugged, leading me to believe there was a deeper issue, water ingress, cable damage, etc. If it was just a faulty RCD why wasnt it replaced, or even the spare on the board used instead.

Can anyone please advise on if i should be worried, or if i should call another electrician to replace the RCD and possibly have to track down the issue.
Many thanks in advance.
 
Hi everyone,

I'm left feeling a little concerned after an electrician visited us to rectify a problem with our ring main, An RCD was tripping solely when the Ring main was on, there were two other breakers for the lighting circuits which would stay on just fine. I figured it would most likely be an appliance causing the issue so turned off every wall socket, then unplugged everything in the house. The RCD would still trip. This was as far as i could investigate so called a local electrician, they came out every quickly.
They were only at the house for about 30 minutes changing things around in our main board, he mentioned that we could probably use more sockets as our house is quite dated and has only one socket in most rooms, so lots of extension cables are being used.
He removed the socket circuit (ring main i think) from that RCD and left it just on a breaker.

my rail previously looked like this <RCD><Light><Light><unmarked (this was the wall socket breaker> gap <RCD><Unknown Breaker><Main Switch>
After the visit it looks like this <RCD><Light> gap <RCD><unknown breaker (now controlling wall sockets)><Main switch>

The left most RCD turns off the lights, the right most RCD doesnt seem to turn anything off when tested. The right most breaker is now what turns my wall sockets off.
I did not test the right hand cluster of RCD and breaker before the electrician came, so i cant be sure what they were connected to or how it was changed.
My main concern now is that my ring main is not covered by an RCD, and that the RCD was tripping with everything unplugged, leading me to believe there was a deeper issue, water ingress, cable damage, etc. If it was just a faulty RCD why wasnt it replaced, or even the spare on the board used instead.

Can anyone please advise on if i should be worried, or if i should call another electrician to replace the RCD and possibly have to track down the issue.
Many thanks in advance.
Some pictures of the consumer unit may help especially one with the cover on and one with it off.

But best advice is to have another electrician take a look at it.
 
If you turn off both rcd's and your sockets stay on... AND if the sockets are not on an RCBO, then yes, it sounds like all he has done is remove them from being RCD protected. If that is the case (impossible to say for sure without being there) then I can't think of any reason you could get away with doing this in a house. 'If' he has done this, then that is truly appaling and incompentent and you should not be paying them a penny. If they are a member of a scheme you should report them.

More importantly, you need to get the fault fixed and the sockets back on a RCD.
 
Thanks for the responses everyone, I'm going to arrange for another electrician to look at it asap monday.

Incidentally, I've attached pictures of my unit.
1000042322.webp
1000042323.webp
1000042324.webp
 
I would want both RCD's to be using the same connections.

One has the Live going through 1-2, and the neutral 3-4.... The other one is Live 3-4 and Neutral 1-2.

The datasheet for the newer version of these does say the 2 pole is NOT polarity sensitive, so it should work as it is.....


but..... butchered i think is the right description
 
You've had a right butcher have a go at that. They may be many things but one isn't an electrician.
More to the point if they have really done that how the hell can they sleep at night!

Whoever has done this needs reporting they should not be anywhere near a fuse board.

This is extremely dangerous!

I don't think a first year apprentice would make that much of balls up of this. Not sure what is the corker here the fact that they couldn't be arsed to find a fault and decided to just forgo RCD protection or the way they have absolutely butchered that bus bar and couldn't be arsed to remove the plastic protection and at least cut the damn thing properly so there is no copper showing and it isn't nudging the RCD into a funny angle!
 
One of the cpcs (earth wires) isn't in the MET (main earthing terminal) as well. Hard to tell, but looks like one leg of the lighting circuit.
 
Guessing that is two lighting circuits with crossed neutrals on the landing light. Odd set up I would also expect immersion and cooker circuits.
 