Solar. How hard can it be?

Right, just had a call from a sort-of-related-that-I've-never-met potential new customer: wants to put a solar array on to the roof of a stables, not for FIT but to charge a battery bank to then run lighting and some low draw stuff. The reason is that there's no other way to get power there.

I'm not MCS (I know that won't matter as it's not for FIT), I've never touched a solar panel in anger before and it's been years since I messed about with accumulators. Don't get me wrong, I understand the theory just never done it in practice.

I don't want to just pass on the job without at least looking at the options first.

What do I need to know, where do I start with this?
 
An 'off the shelf kit' wouldn't be suitable at all would it???

I didn't know they existed! As in, a kit that's panels > batteries > 230v ?
 
I too know nothing sensible about solar installation so I thought I should post:whatchutalkingabout!

You want to design a system that has over capacity so that you can supply enough power to run all they want to run at any time, with the obvious limitation that it will not work once they plug in the electric heater.
This does mean getting more panels than you might need to do the basics but prevents later problems.
It will also avoid the batteries being drained even if they are deep cycle. Though the charge controller should cut out once the batteries start to go flat.
The costs of the maintenance of the installation are also significant as the batteries do not last all that long and are very costly for the quality ones, that said I have run a solar panel for a small pump for over four years on a second hand UPS battery!
Check load required, get batteries that can supply this easily, get enough panels to be able to Charge said batteries, get a charge controller (consider an MPPT controller) that can handle the current, get an inverter that does not need an external power supply to work, align the panels to the correct angle , connect up and leave!

But what do I know, this could all be rubbish.
 
step 1 - calculate peak load and average daily winter load.
step 2 - revisit step 1 and look at every cost effective method of reducing peak and average loads, as this is generally a lot cheaper than buying the extra batteries and panels - ie LED lighting, energy efficient kit, and agreeing with customer if they're prepared to accept that at some points with several days of low sun they may need to temporarily restrict their usage in order to avoid spending several grand extra.
step 3 - design a system to meet peak load (this is the easy bit, as you just buy the inverter that matches that requirement), and average daily winter load - the hard bit as this relates to the number of batteries needed to store sufficient power over the maximum number of no sun days, as well as the number of panels needed to keep the batteries charged up on average through the winter.

also, remember that panels need to be run in parallel not series at something like 30V panels for a nominally 24v system, which means high ampages, and big cables, NOT standard 4-6mm PV cables used on high voltage low ampage grid connect systems.

and don't forget that certain members may have a few end of line panels kicking around that they could let go cheaply as they can't really get used on a grid connect system. (we've got 4 x 235Wp 30V poly panels that arenow discontinued, that I'd suspect would be reasonable for low energy lights and occasional inverter loading).
 
Well I'm going to take a look on Friday so I'll try to make some sense of what it is that they actually need to have. The guy said to me on the phone that the reason he's looking at this is because the DNO have said no more power off the nearest pole and quoted £5k to upgrade the transformer. But I really can't imagine that a 'no load' for some led lights in a stable would be an issue?
 
OKaaaayyy..... had a look earlier and it's either far simpler or more difficult than I thought: All he wants to do is run some led batten or flood lights, that's it. 2 stables, 1 tack room. He was thinking that you could just charge a 12v battery from a 12v panel and use it direct on to a 12v led light but obviously I've pointed out that it's not quite that simple.

So, all in there's little in the way of current draw, there's a south ish facing roof available and theoretically the job can be all ELV start to finish.

Would 2 x 30v panels be sufficient to trickle charge 2 x deep cycle 12v's? And if so, what device would you use as a charge controller?
 
Hmm thinking out loud (you know what I mean) seems like you can run on a 12V system. So you would want 12V panels and 12V charge controller and 12V batteries, simples.
Looks like you would be using maximum 200W 8hrs a day (if it is a remote area).
Your panels will provide about 50% of the rated capacity (total guess for British weather) six hours per day on average.
so need 500W of mono/poly crystalline solar panels to supply batteries capable of running at least one light say 20W for 8 hrs when someone leaves the light on (but have controlled lights on timers, sensors and such) so say a 20Ah battery (have two for security of power supply).
Could use a 20amp charge controller and probably not worth the outlay for MPPT.

And this is then well over specced but should set you back about £500 (less sensors), just my thoughts and making some very big assumptions.

If you were to instill some power saving sense in the customer then you should be able to half spec this and provide reasonable power.

Solar designers will try and minimise as far as possible the available power and supply a cheaper system.
 