Got called to an RCD tripping issue yesterday.......TT,with 100ma S type main switch. Global Ir tested and got a dead short,broke it down to kitchen lights. Disconnected from DB and tested cable on it's own...clear! Scratch head and test again...dead short! Check in kitchen and find a dozen GU10 LED downlights,go to center of run and split the cables. Once again fault appears then disappears randomly.
Tracked it down to one of the LED lamps....there was an intermittent short between the lamp pins and metal body of the lamp,when in the earthed downlight it was the cause. Lamp removed and all was well. Checked all the others with a soft IR test between the pins and lamp body and got some low readings...as low as 0.4 megs. One to look out for,and possibly a shock hazard if an attempt is made to change one of these with power still on..... Lamps were 'Fusion' brand BTW.
Tracked it down to one of the LED lamps....there was an intermittent short between the lamp pins and metal body of the lamp,when in the earthed downlight it was the cause. Lamp removed and all was well. Checked all the others with a soft IR test between the pins and lamp body and got some low readings...as low as 0.4 megs. One to look out for,and possibly a shock hazard if an attempt is made to change one of these with power still on..... Lamps were 'Fusion' brand BTW.