Hi Has any one had any issues with Newlec B 32A MCB SB breakers? Had an issue with one tonight tested ok on Friday but tonight no voltage from outlet side?
 
Maybe old stock as there was a huge wylex/volex /newlec recall a while ago , this one may have slipped through the net.

Nick
 
Just to point out the recall did not include 32 amp mcb's it was 6 10 and 16 amp , ensure you have inserted the MCB into position correctly if you have missed the bus bar with the clamp you may well have tightened the clamp on its self so easy to do , and might just have made contact when you were there worth checking
 
I've inspected several Newlec CUs recently and I haven't found one from the recall list, only 6,10 and 16A are in the recall.
 