UK NICEIC - EICR tickboxes.

I always seem to think twice about this tickbox:
1768667233405.png

In any normal TN-S or TN-C-S arrangement RCD's are not primarily for fault protection. My question is do i leave this as N/A unless it is a TT arrangement and i have an upfront 100ma RCD for fault protection? Or do i tick it anyway? as the RCD's/RCBO's intended for additional protection will inherently provide fault protection as well?
 
No only tick if they provide fault protection which can be applicable to TN systems as well.
I'd have loved to have been witness to seeing you at one of your yearly assessments Westward, you'd have had the assessor tied up in knots!
"No, you're wrong, if you look at reg 548.8.8 dash B, note (ii) you'll see that it points you to 23.879 dash 7hw which tells you to check BS 4567. You see, it's quite clear really"
 
I always seem to think twice about this tickbox:View attachment 124322
In any normal TN-S or TN-C-S arrangement RCD's are not primarily for fault protection. My question is do i leave this as N/A unless it is a TT arrangement and i have an upfront 100ma RCD for fault protection? Or do i tick it anyway? as the RCD's/RCBO's intended for additional protection will inherently provide fault protection as well?
As mentioned by others they are being used for additional protection and not fault protection. But I just wanted to congratulate you for acknowledging this and asking, as far too many incorrectly tick this box.
 