No discrimination, no problem???

There is no requirement to rcd the swa to db3.! But there's nothing wrong with the two rcds just no discrimination.! If it gives you peace of mind and the customer is happy to pay for the extra protection carry on. What earth electrode was in place at db3 through curiosity?
 
Not sure yet, try and get a two piece 8ft jobby in but if not one of those 4ft tent pegs I expect. See what Ra we gets.....
 
It wouldn't cost that more then to upgrade to 10mm 3core, then you've got a decent earth also will be of adequate size for the bonding at the outbuilding and you wouldn't have to bother installing rods, etc.
 
Last edited by a moderator:
Yeah true still more expensive than 2 core and rod hence original design. Splitting hairs but 6mm2 2core easier/quicker to work with than the 10mm2.....and extraneous conducive parts....
Don't want to open the exporting earth debate. Thanks for the comments, I've got the info I needed, will go through it with matey tomorrow.
 
Last edited by a moderator:
Because in the event of a neutral earth fault its a pain in the backside and how are you going to carry out the appropriate RCD tests when your tester will be set to 30ma? How will you know what RCD your readings are from when testing when both have tripped?

By connecting the "live" test probe to the outgoing "L", and the other to the incoming "N"? That's what I do when there's an upstream RCD as it doesn't cause an out of balance line / neutral current for the first RCD.
 