you could demonstrate to your friend what a shock is like by meggering him lol (not really)
he will then go with the earthing option
the no earth scenario was ok donkeys years ago double insulated singles etc with PLASTIC FIXTURES AND FITTINGS
not the done thing today, a sparky wont touch it and your right not to be doing the metal fitting
ask him the question if you changed the light fitting and he went to change a lamp at a later date and had a shock DIRECT CONTACT would he call you to give you a peice of his mind???i would assume hes got the old consumer unit and rewireable fuses too
so the no earthing scenareo was ok was it?....so whats the purpose of earthing then?....
 
It's funny you mention Thailand because I have a few friends there.

From the little information I can piece together there are no electrical standards and no electrical regs available to guide electricians.

Apparently a lot of the installations have no earth at all, they were based on two wire systems sort of like an earth free IT system but unfortunately over time the insulation has broken down and has begun to leak with no ADS in place in case of an earth fault.

Apparently there are a lot of fatal electric shocks in Thailand.

This is all heresay because I have never actually visited the country myself but it seems in Thailand the idea of an earth circuit was considered a waste of time.

It may be different in the more modern areas.
 
It's funny you mention Thailand because I have a few friends there.

From the little information I can piece together there are no electrical standards and no electrical regs available to guide electricians.

Apparently a lot of the installations have no earth at all, they were based on two wire systems sort of like an earth free IT system but unfortunately over time the insulation has broken down and has begun to leak with no ADS in place in case of an earth fault.

Apparently there are a lot of fatal electric shocks in Thailand.

This is all heresay because I have never actually visited the country myself but it seems in Thailand the idea of an earth circuit was considered a waste of time.

It may be different in the more modern areas.
sort of like a `post code lottery` then..lol....
 
Having no earth reference in a system and supply is a brilliant system,live straight down to earth and no effects
icon6.png

That is until the second fault scenario ,then it tends to become worthwhile
icon12.png
 
Aye, you never know.

"Phuket - A Russian tourist was electrocuted and restaurant manager severely injured in a power leakage at a swimming pool Wednesday night, police said.

Police said Fedor Samsonov, 45, was killed in the swimming pool of Dewa Hotel on the Karon Beach.

Surasak Phetsut, 33, the restaurant manager, was severely injured when he tried to rescue the tourist.

Witnesses told police that Samsonov was exiting the pool when he touched the rail of the pool and was electrocuted by the leaked power."

Russian tourist electrocuted in swimming pool of Phuket hotel - The Nation

A classic example.
 
Aye, you never know.

"Phuket - A Russian tourist was electrocuted and restaurant manager severely injured in a power leakage at a swimming pool Wednesday night, police said.

Police said Fedor Samsonov, 45, was killed in the swimming pool of Dewa Hotel on the Karon Beach.

Surasak Phetsut, 33, the restaurant manager, was severely injured when he tried to rescue the tourist.

Witnesses told police that Samsonov was exiting the pool when he touched the rail of the pool and was electrocuted by the leaked power."

Russian tourist electrocuted in swimming pool of Phuket hotel - The Nation

A classic example.
Phuk that for a game of soldiers. Bit much for a leaking swimming pool. Once more, send for a plumber.
 
...
ask him the question if you changed the light fitting and he went to change a lamp at a later date and had a shock DIRECT CONTACT would he call you to give you a peice of his mind?....

Why would he get a direct contact shock? Having an earth or not is nothing to do with direct contact.
 
Aye, you never know.

"Phuket - A Russian tourist was electrocuted and restaurant manager severely injured in a power leakage at a swimming pool Wednesday night, police said.

Police said Fedor Samsonov, 45, was killed in the swimming pool of Dewa Hotel on the Karon Beach.

Surasak Phetsut, 33, the restaurant manager, was severely injured when he tried to rescue the tourist.

Witnesses told police that Samsonov was exiting the pool when he touched the rail of the pool and was electrocuted by the leaked power."

Russian tourist electrocuted in swimming pool of Phuket hotel - The Nation

A classic example.
was that exiting it ..or `exiteing` it..lol....
 
thats insane.....so they have no concept of ADS and disconnection times etc?....mad....
Most of them are Bhuddists, when your time has come, your time has come, it's destiny. I'd love to work out there for a few months just to see what its like.
 
Obviously nothing bonded back to the MET for the OCPD to see a fault exists!! Generally, All metal steps, diving boards etc, have a bonding terminal incorporated into there fixing systems. These are normally taken to the re-bar of the swimming pool, which is in turn bonded back to the MET or the EMT of the pools electrical systems in the plant room!! I doubt very much if there was any form of RCD protection incorporated, especially if it was an older Hotel!!
Even if there was, if it had been causing nuisance tripping in the past, it would have been quickly by-passed, ...not replaced!! lol!!
 