NO RCD on Sauna???
HappyHippyDad
Supporter
I am designing a circuit for a sauna which will be located at the bottom of a garden.
The house is TT.
I initially was going to feed it from a 30mA RCBO.
However, i have requested the MI's and they state IN BOLD, that the sauna must not be powered from an RCD.
Is this right? A wet room in the garden with no RCD?
If it is, then I will need to fit an S type 100mA RCD for the supply down the garden.
AI did mention about the 'baking' test. It suggested that the sauna only trips during initial set up. if I let it run for 20-30 mins without RCD, I can then fit a 30mA RCD. Sounds a bit risky.
Tricky one as you don't really want to include it as a departure but you could cite manufacturers instructions. Where is it made and can these instructions be relied upon for the UK?
Once I'd seen the reg I didn't think it was tricky at all Westward. 'RCD protection need not be given to the heater'. Plus the MI say no RCD to the heater. I'm happy with that! 100mA time delayed RCD for the fault protection on the SWA leading down to the small CU from a switch fuse.
I don't think you read it through! :rolleyes: :D