Need help!
I have 3 acb NW (Schneider) in three switchgears side by side. N1(from transformer 1)-Coupling-N2(from Tr2), interlocking 2/3. I use both mechanical and electrical interlocks, but they can only correctly operate individually. When I did them simultaneously, the operations are not correct anymore. I don't know why!
Did anybody ever fix this before?
Thanks
 
What sort of interlocking is used? Castell mechanical interlocks are quite robust but you can force and damage them. If you’ve damaged it then I wish you luck, by nature the locks are difficult to strip and repair. It’s often better to order replacements.

You need to give more information and also describe what you are trying to do. You can defeat inter-locks but you have to be 200% sure of what you are doing and why.
 
As Tony stated, we need to know what you are trying to do or achieve, also Schneider do a non-key mechanical interlocking system, ...is this what you have, or the trapped Key interlocking system?? Are both TR1 and TR2 being supplied from the same source or from different MV networks?? Is this a new installation, or one that has been previously working fine, or has never worked correctly??

Please give as much information as you can, if possible with photo's showing switchboard ACB cubicle's external and internal (open door)
 
A normal lay out would be:
[TABLE="width: 192"]
[TR]
[TD="width: 64, bgcolor: transparent"]Tx 1[/TD]
[TD="width: 64, bgcolor: transparent, align: right"]1[/TD]
[TD="width: 64, bgcolor: transparent, align: right"]1[/TD]
[TD="width: 64, bgcolor: transparent, align: right"]0[/TD]
[/TR]
[TR]
[TD="bgcolor: transparent"]B-S[/TD]
[TD="bgcolor: transparent, align: right"]0[/TD]
[TD="bgcolor: transparent, align: right"]1[/TD]
[TD="bgcolor: transparent, align: right"]1[/TD]
[/TR]
[TR]
[TD="bgcolor: transparent"]Tx2[/TD]
[TD="bgcolor: transparent, align: right"]1[/TD]
[TD="bgcolor: transparent, align: right"]0[/TD]
[TD="bgcolor: transparent, align: right"]1[/TD]
[/TR]
[/TABLE]

Are you trying to close all three?
 
A normal lay out would be:
[TABLE="width: 192"]
[TR]
[TD="width: 64, bgcolor: transparent"]Tx 1[/TD]
[TD="width: 64, bgcolor: transparent, align: right"]1[/TD]
[TD="width: 64, bgcolor: transparent, align: right"]1[/TD]
[TD="width: 64, bgcolor: transparent, align: right"]0[/TD]
[/TR]
[TR]
[TD="bgcolor: transparent"]B-S[/TD]
[TD="bgcolor: transparent, align: right"]0[/TD]
[TD="bgcolor: transparent, align: right"]1[/TD]
[TD="bgcolor: transparent, align: right"]1[/TD]
[/TR]
[TR]
[TD="bgcolor: transparent"]Tx2[/TD]
[TD="bgcolor: transparent, align: right"]1[/TD]
[TD="bgcolor: transparent, align: right"]0[/TD]
[TD="bgcolor: transparent, align: right"]1[/TD]
[/TR]
[/TABLE]

Are you trying to close all three?

Its the interlock 2/3, and I am not trying to do the thing that cant be done.
The mechanical interlock uses cables, the electrical interlock are 2 NC contacts in parallel of 2 CBs connects in serial to closing circuit of the rest. Closing and opening orders using push buttons.
When I did operate separately mechanical and electrical interlock, it was ok: when 2 CBs are closing, the rest can not close. But when I tried to operate simultaneously, it was not ok anymore. Ordered Tx1 closed but immediately returned open, Tx2 and B-S were ok,.
Its new installation, both Tr1 and Tr2 are from the same source of MV network.
Thank all for your cares
 
For the electrical interlocks, does the shut trip energise when you try to close Tx1?
From your description I would guess you have an auxiliary contact misaligned or damaged in Tx2 or B-S ACB’s.
When you try to close Tx1 ACB the shunt trip series contact is making and causing the ACB to immediately open.
Please see the drawing. Shunt trip coils are shown as ACBx.

View attachment 14760
 